Cummins RS30 Specs at a Glance

Specification Cummins RS30
Natural-gas / propane output 30 / 30 kW
Rated current at 240V, NG / LP 125.0 / 125.0 A
Engine QSJ2.4, 2.4L turbocharged and aftercooled inline-four
Speed 1,800 rpm
Weight 1,231 lb
Main generator breaker 150 A
NG at half / full load 219 / 380.9 ft³/hr
LP vapor at half / full load 95.9 / 164.1 ft³/hr
Dimensions, L × W × H 94 × 34 × 45.5 in
Published Sound Level 1 65 dBA at 23 ft
Controller PowerCommand 1.1
Starting battery 12V negative ground; manufacturer lists 550A capacity at 0–32°F

Scope: U.S. 120/240V single-phase, 60Hz. Figures follow NAS-5776-EN, July 2021; altitude, temperature, fuel quality and ordered options may change performance. Confirm the supplied unit’s specification and serial-number documentation.

Source: Cummins NAS-5776-EN, July 2021 specification.

Is the Cummins RS30 Really 30kW on Natural Gas?

Yes. The linked specification rates the RS30 at 30kW on both natural gas and propane in the 120/240V single-phase configuration. Use the matching document revision rather than an older fuel rating. Environmental derating and fuel supply can reduce available output.

Source: Cummins NAS-5776-EN, July 2021 specification.

How Much Does a Cummins RS30 Cost?

Get an itemized local installed quote; an equipment price does not cover the complete project. No verified current model-specific retail price is asserted here. Require separate line items for the generator and options, automatic transfer switch, battery, delivery and lifting, foundation, electrical work, fuel piping or tank, permits, commissioning and any meter upgrade or load controls. Compare equal scopes from qualified local installers. Remote siting, trenching, service changes and cold-weather accessories can materially change the total. Our whole-house generator cost guide explains the scope to compare.

Source: Cummins home-generator purchasing information.

How Much Does an RS30 Cost Installed?

Get an itemized local installed quote; an equipment price does not cover the complete project. No verified current model-specific retail price is asserted here. Require separate line items for the generator and options, automatic transfer switch, battery, delivery and lifting, foundation, electrical work, fuel piping or tank, permits, commissioning and any meter upgrade or load controls. Compare equal scopes from qualified local installers. Remote siting, trenching, service changes and cold-weather accessories can materially change the total. Our whole-house generator cost guide explains the scope to compare.

Source: Cummins home-generator purchasing information.

RS25 vs RS30: Is the Extra 5kW Worth It?

Compare running output on the fuel you will use, motor-starting performance and the complete installed system.

The RS30 fits properties whose simultaneous demand justifies 30kW and the fuel supply and footprint of a liquid-cooled system. A small generator-only price difference does not establish a small installed difference: check fuel demand, delivery access and the exact ordered voltage/phase. Compare written quotes for the exact packages rather than carrying forward older price gaps. Ask for the alternative’s current single-phase specification and a written quote before comparing the capacity step.

Source: Cummins NAS-5776-EN, July 2021 specification.

RS30 vs. RS36: Is the Extra Capacity Worth It?

Compare running output on the fuel you will use, motor-starting performance and the complete installed system.

Model NG / LP output Starting at 30% voltage dip Speed
RS30 30 / 30 kW Verify ordered alternator 1,800 rpm
RS36 36 / 36 kW Verify ordered alternator 1,800 rpm

The RS30 fits properties whose simultaneous demand justifies 30kW and the fuel supply and footprint of a liquid-cooled system. A small generator-only price difference does not establish a small installed difference: check fuel demand, delivery access and the exact ordered voltage/phase. Compare written quotes for the exact packages rather than carrying forward older price gaps.

Source: Cummins NAS-5776-EN, July 2021 specification.

How Much Natural Gas Does the RS30 Use?

The Cummins RS30 uses 219 cubic feet per hour at 50% load and 380.9 at full load on natural gas.

Load Natural gas, ft³/hr
25% 147.6
50% 219
75% 300
100% 380.9

These are typical manufacturer consumption figures, not guaranteed consumption at a property.

Source: Cummins NAS-5776-EN, July 2021 specification.

Will My Existing Natural-Gas Meter Handle an RS30?

Your utility and installer must check capacity under the combined demand of all gas appliances. The RS30 alone needs 380.9 ft³/hr at full load in the linked table. Meter capacity, service pressure, regulator capacity, pipe length, fittings and pressure drop all matter. A larger inlet connection does not establish that the existing supply is adequate.

Source: Cummins NAS-5776-EN, July 2021 specification.

How Much Propane Does the Cummins RS30 Use?

The Cummins RS30 uses 95.9 cubic feet per hour at 50% load and 164.1 at full load on LP vapor.

Load LP vapor, ft³/hr Approx. liquid propane, gal/hr
25% 66.4 1.82
50% 95.9 2.64
75% 129.1 3.55
100% 164.1 4.51

These are typical manufacturer consumption figures, not guaranteed consumption at a property. Gallons are calculated using the manufacturer’s 36.39 ft³ of LP vapor per liquid gallon. The adjacent m³/hr column is cubic metres of vapor, not gallons; the two values can look misleadingly similar.

Source: Cummins NAS-5776-EN, July 2021 specification.

How Long Will a 500-Gallon Propane Tank Run an RS30?

At an assumed 80% fill, a nominal 500-gallon tank contains about 400 gallons. At constant full load, 400 ÷ 4.51 gives roughly 89 hours; at half load, 400 ÷ 2.64 gives roughly 152 hours.

This calculation uses unrounded fuel rates and the manufacturer’s vapor-to-liquid conversion. It is not a usable-runtime guarantee: keep a reserve and allow for other propane appliances. Temperature, tank vaporization capacity, regulator size and minimum fuel pressure can limit operation before the tank is empty. Have the propane supplier size delivery at full-load demand and the coldest expected conditions.

Source: Cummins NAS-5776-EN, July 2021 specification.

Is the Cummins RS30 65 dBA or 60 dBA?

The July 2021 RS30 sheet lists 65 dBA at 23 ft with Sound Level 1. The older April 2015 sheet lists 60 dBA with Sound Level 2. These refer to different enclosure configurations, not interchangeable measurements of every unit. Older Cummins Sound Level 2 specification. Ask which enclosure and sound upgrade the quote includes. Distance, load, reflections, siting and local noise rules affect what neighbors hear.

Source: Cummins NAS-5776-EN, July 2021 specification.

Cummins RS30 vs Kohler 30RCLA

Compare running output on the fuel you will use, motor-starting performance and the complete installed system.

The RS30 fits properties whose simultaneous demand justifies 30kW and the fuel supply and footprint of a liquid-cooled system. A small generator-only price difference does not establish a small installed difference: check fuel demand, delivery access and the exact ordered voltage/phase. Compare written quotes for the exact packages rather than carrying forward older price gaps. Review our Kohler vs. Cummins comparison.

Source: Cummins NAS-5776-EN, July 2021 specification.

Cummins RS30 vs Generac XG 32kW

Compare running output on the fuel you will use, motor-starting performance and the complete installed system.

The RS30 fits properties whose simultaneous demand justifies 30kW and the fuel supply and footprint of a liquid-cooled system. A small generator-only price difference does not establish a small installed difference: check fuel demand, delivery access and the exact ordered voltage/phase. Compare written quotes for the exact packages rather than carrying forward older price gaps. Review our Generac vs. Cummins comparison for an equivalent-system shortlist.

Source: Cummins NAS-5776-EN, July 2021 specification.

Which Is More Reliable: Cummins, Kohler or Generac?

Compare running output on the fuel you will use, motor-starting performance and the complete installed system.

The RS30 fits properties whose simultaneous demand justifies 30kW and the fuel supply and footprint of a liquid-cooled system. A small generator-only price difference does not establish a small installed difference: check fuel demand, delivery access and the exact ordered voltage/phase. Compare written quotes for the exact packages rather than carrying forward older price gaps. Review our Generac vs. Cummins comparison for an equivalent-system shortlist. Review our Kohler vs. Cummins comparison. No controlled comparative failure-rate dataset is available here; owner anecdotes do not establish a reliability winner. Nearby authorized service, commissioning and maintenance are practical selection criteria.

Source: Cummins NAS-5776-EN, July 2021 specification.

What Warranty Does the RS30 Actually Have?

The RS30 and RS36 liquid-cooled sheets list a two-year base standby warranty. Cummins’ coverage brochure distinguishes 1,000-hour and unlimited-hour configurations; confirm the exact applicable limit in the serial-specific statement. Coverage for parts, labor and travel can vary by year, package and warranty extension. The generator and transfer switch have separate terms; RA/RSS ATS coverage is listed at two years. Keep commissioning and maintenance records and obtain the complete written terms before purchase.

Sources: Cummins home-generator FAQ, Cummins warranty coverage brochure.

Source: Cummins NAS-5776-EN, July 2021 specification.

Does the RS30 Include an Automatic Transfer Switch?

Confirm the exact package and transfer-switch model in writing. The liquid-cooled specification lists the automatic transfer switch as sold separately. Have the installer specify amperage, voltage, phase, service-entrance rating, number of panels and any load-management controls. The generator’s output amperage and the utility-service or ATS rating are different design limits.

Source: Cummins NAS-5776-EN, July 2021 specification.

At 240V single-phase, 30kW on natural gas is approximately 125.0A, not 200A or 400A. Service amperage is not the home’s measured simultaneous demand.

Does a 400A House Need an RS30 or Larger?

Confirm the exact package and transfer-switch model in writing. The liquid-cooled specification lists the automatic transfer switch as sold separately. Have the installer specify amperage, voltage, phase, service-entrance rating, number of panels and any load-management controls. The generator’s output amperage and the utility-service or ATS rating are different design limits.

Source: Cummins NAS-5776-EN, July 2021 specification.

At 240V single-phase, 30kW on natural gas is approximately 125.0A, not 200A or 400A. Service amperage is not the home’s measured simultaneous demand.

Does the RS30 Include a Battery?

Include the starting battery explicitly in the quote. The liquid-cooled sheet specifies 12V negative-ground starting and a 550A battery-capacity requirement at 0–32°F; confirm the approved battery group, terminals and cold-weather provisions for the ordered unit.

Source: Cummins NAS-5776-EN, July 2021 specification.

Does the RS30 Have Remote Monitoring?

Confirm remote monitoring as an ordered accessory for this controller. The RS liquid-cooled sheet lists a PowerCommand 500 internet-monitoring device among accessories. Do not assume it includes the same built-in connectivity as the air-cooled line. Get compatibility, hardware, commissioning and any service charges in the quote.

Source: Cummins NAS-5776-EN, July 2021 specification.

See Cummins Connect Cloud.

What Maintenance Does the Cummins RS30 Need?

For the Spec A QSJ2.4 units covered by A045R242 Issue 12, oil and filter service is due after the first 50 hours, then every 200 hours; the table also specifies the annual interval, whichever comes first. Check oil and coolant daily or every 24 operating hours. The manual lists air-cleaner replacement at 100 hours, spark-plug inspection at one year/200 hours, and coolant replacement at two years. This July 2018 manual explicitly covers C30 N6 and C36 N6 Spec A; do not apply its schedule automatically to Spec B or another revision. Have the servicing dealer supply the serial-specific manual and confirm any updated schedule.

Source: Cummins operator manual A045R242, Issue 12 (Spec A).

Can the RS30 Be Used Off Grid?

This is an emergency standby generator for interruptions to a normal utility supply. A standby rating does not authorize continuous prime-power or off-grid operation. The air-cooled sheet explicitly excludes those applications from its emergency-standby warranty; liquid-cooled sheets describe EPA stationary emergency use. Obtain written application approval and applicable warranty terms before planning regular daily generation.

Source: Cummins NAS-5776-EN, July 2021 specification.

What Is the RS30 “Spec-B” Version?

Spec B identifies a manufacturing/specification revision, not simply a transfer-switch bundle. Confirm model, spec letter, serial number, voltage, phase and part number with the dealer. A specification or service schedule labeled Spec A may not apply. Match the operation, installation and service manuals before ordering parts or scheduling maintenance.

Source: Cummins operator manual A045R242, Issue 12 (Spec A).

Will the RS30 Run My Whole House?

Only if the verified simultaneous running and starting loads fit the fuel-specific rating. The RS30 delivers 30kW on natural gas and 30kW on propane. It fits properties whose simultaneous demand justifies 30kW and the fuel supply and footprint of a liquid-cooled system. Electric heat, ovens, EV charging, pumps and multiple compressors can exceed the plan. A whole-service transfer switch does not mean every appliance can run together. Organize a load list with our generator size calculator, then have the installer verify the design.

Source: Cummins NAS-5776-EN, July 2021 specification.

Our Take: Where the Cummins RS30 Fits

The RS30 fits properties whose simultaneous demand justifies 30kW and the fuel supply and footprint of a liquid-cooled system. Choose from the load calculation and service support, then compare equal installed scopes. A model number or a small equipment-price gap is not sufficient reason to upsize.

Sources and Model Verification

These are manufacturer-authored documents; some PDFs are hosted by suppliers. Specifications are revision-specific. Confirm the ordered model, serial number, spec letter, voltage, phase, fuel, enclosure and warranty statement with the dealer. The linked liquid-cooled operator manual applies to Spec A, and should not substitute for a later unit’s service instructions. Confirm current equipment and installation pricing in a written local quote.